181025-0821 EDT
buffalonymann:
I believe Russs57's point is that if you use your PLC output to control an ordinary electromagnetic relay, such as a P&B KUP, with mechanical contacts on its output, then you can obtain an output contact with very low leakage current compared typical SSRs.
The Crydom drawing shows one output switch terminal pair as A1-A2, another as B1-B2, and the third as C1-C2. I don't believe any one of these pairs is your L1-L2.
Gar, I'm calling them L1 and L2 out of habit, so L1 would be A2 and L2 would be B2. We're seeing 190VAC across A2(L1) and B2(L2) and C2(L3)
Considering only one SSR contact in the Crydom package, for example A1-A2, then is that contact the switch in a simple single phase series circuit consisting of a 240 V source, the A1-A2 contact, and a load resistor? I am concluding that is what you have said. In that series circuit do L1 and L2 refer to the load resistor terminals? If not, then where in the circuit are L1 and L2?
My bad for not being more precise - I overlooked that you have not seen a wiring diagram of our system.
We have 3 phase Delta 240VAC for supply power. Phase A to A1\Phase B to B1\Phase C to C1. Output is A2, B2, C2. Single Phase heaters are across A2 and B2, B2 and C2, A2 and C2
PLC output to control (120VAC) circuit
For a high power load on the output of an SSR the snubber leakage current will produce no significant voltage across that load resistance. If you see a noticeable voltage, but not full voltage, across the load, then the SSR is conducting during a portion of the AC cycle. It appears that your SSR is conducting over some portion of the cycle. In my OAC5 test the SSR had three distinct states --- no conduction, looking like a 1/2 wave rectifier, and full conduction, and very touchy input control voltage to get the 1/2 wave rectification. I can visualize in your case that at 18 V there is some partial cycle conduction, and not so touchy as in the case of my OAC5.
.
Ok, what you say about the conduction during part of the cycle is a feasible diagnosis, perhaps that is what we are seeing. My company didn't want to spend money to buy a scope for me, so I'm stuck with a $400 piece of hardware that allows me to use my laptop as a scope, problem is it's rated at 30 volts (rolls eyes) I'm dealing with a management group without any technical background whatsoever, and never have a clue about what I'm telling them.