Can someone tell where it states that the #6 bonding wire has to be connected to the main panel and not a sub panel ground bar?
Not in the NEC. NEC has no rules concerning CSST other then that it is metallic gas piping and must at least be bonded by the EGC of the branch circuit likely to energize it.Can someone tell where it states that the #6 bonding wire has to be connected to the main panel and not a sub panel ground bar?
As I said - not in NEC. NEC is fine with bonding it with 12 AWG if only circuit that is likely to energize it is a 20 amp circuit, and doesn't even require it to be "bond wire" but rather just be the EGC of the circuit that may energize it. Gas valve in a furnace is likely bonded to the EGC of the furnace branch circuit and also bonded to the gas supply piping - In that case NEC requirements are met. Gas code or product instructions for CSST being used may require more then that though.Yeah i pretty much came to the same conclusion Kwired
all i found was>>>
250.104 (B) Other Metal Piping
choices 1 thru 5 , with ref to Table 250.122
I just can't see a piece of #12 being used, pretty sure most any 'bond cu' , or that which would fly around solo would be #8 ,fairly prevalent thru the code
~RJ~
250.104 (B) (3) in the 2014 NEC states that you can bond the gas piping system to the grounded conductor at the service (which is the neutral).Can someone tell where it states that the #6 bonding wire has to be connected to the main panel and not a sub panel ground bar?
250.104 (B) (3) in the 2014 NEC states that you can bond the gas piping system to the grounded conductor at the service (which is the neutral).
My thought as well, also why isn't this another reason for requiring an intersystem bonding termination? It is supposed to be there for others to use and not have to enter the electrical enclosures.So, why aren't the gas guys doing it?
~RJ~
good point, in that respect the nec is being very accomodating of other trades ~RJ~
Of the few I have installed, most got split-bolted to the GEC in the crawl space.I don't know what CSST instructions say but many seem to think it must go to the electric panel and not to the ISBT though.
What few? CSST bonding or the ISBT?Of the few I have installed, most got split-bolted to the GEC in the crawl space.
CSST bonding; I don't know what ISBT is. :?What few? CSST bonding or the ISBT?
CSST bonding; I don't know what ISBT is. :?
Consist of a set of terminals with the capacity for connection
of not less than three intersystem bonding conductors
Can someone tell where it states that the #6 bonding wire has to be connected to the main panel and not a sub panel ground bar?
Is there anywhere in the gas code that states the connection must be continuous? I don't think so so if the equipment grounding conductor to the sub panel is a #6 then the csst bonding should be allowed to connect to that panel.