petersonra
Senior Member
- Location
- Northern illinois
- Occupation
- engineer
Case in point: My 1957 house just had the gas line to the water heater (in the carport) rust through. In such a repair, I expect many guys would simply cut the pipe, thread the ends, and use a length of CSST. Remember: they're not allowed to use unions under the house, and taking the line apart from the end is a lot more work!
Neither fuel gas code restricts the use of unions in a crawl space, only in concealed locations, with the exception in the National fuel Gas Code that will allow a repair in a concealed location to use a union and center punch the retaining nut to prevent it from backing apart.
In your scenario of black pipe and adding a section of CSST to a stationary piece of equipment a # 6 copper conductor or equivalent would need to be run to bond the CSST back to the Grounding Electrode System.
Wouldn't it make sense to allow the bond in such a case to be made to the other end of the black pipe and let the black pipe be the GEC back to the bonding point? It seems to me that no matter what you do the black pipe is going to act as a GEC anyway in this kind of case. .