Update. Mr. Inspector returned my call. Seems he is quite familiar with CSST as there WAS a house right down the street from this one, where 7KV primary was introduced to the neutral service entrance conductor.
Anyway, he said that I should do what was required by 250.93 and the listing/labeling (and tell the Plumber to pound sand). He then went on to tell me, that if I should do less than code minimum, then the monkey is on my back, which I already knew. However, should I do more than what is required by code, than I am saying that I feel there is a potential danger, and if my exceeding code still allowed lightning (or the introduction of primary voltage) to cause a fire and/or injury, then I am putting a larger monkey on my back.
Anyway, he said that I should do what was required by 250.93 and the listing/labeling (and tell the Plumber to pound sand). He then went on to tell me, that if I should do less than code minimum, then the monkey is on my back, which I already knew. However, should I do more than what is required by code, than I am saying that I feel there is a potential danger, and if my exceeding code still allowed lightning (or the introduction of primary voltage) to cause a fire and/or injury, then I am putting a larger monkey on my back.