230.70 says the service disconnecting means shall be located "either outside of a building or structure or inside nearest the point of entrance of the service conductors." So this allows the unfused conductors to come out of the floor inside a building, going straight into a disconnect, a panel with a main, or switchgear. Does this mean a CT cabinet or feed-through meter cannot be in the building? With an indoor CT cabinet, the disconnecting means is not at the nearest point of entrance. Am I seeing this clearly?