090317-1255 EST
richxtlc:
Thanks.
The AS and VS and their associated meters are of no importance to the question of CT's polarity unless they are phase sensitive meters. Whether MFM requires a particular polarity would depend upon what the MFM does. Assuming that MFM has nothing to do with both the upper and lower A, B, and C, then it is of no concern to the question of the differing polarity of the upper and lower CTs.
Remaining is the relationship of ABC of the top CTs to ABC of the bottom CTs. Whether K1 (key interlock) is open or closed it does not change the the current relationship between the top and bottom CTs. If the switch is open, then none of the CTs have any current flow. If closed, then the CTs on each line see the same current.
Therefore, it would look like the only purpose of the paired CTs in this phasing arrangement would be as a means to detect a CT circuit failure. So what does the Schwetizer Engineering differential relay do and does it make use of the information from the upper and lower CTs. If not, then why two sets of CTs?
Both the MFM and SR750 rectangles show the 3 phase input voltages, but no description of any other inputs and how the data is processed. If MFM is calculating power, and related items that need phase information, then polarity at various points is important.
It seems the real question is what the MFM, SR750, and SEL387L do and what are all the inputs and outputs? There seems to be an RS485 connection to SR750 and one to MFM for output.
If the lower ABC does not relate to the upper ABC, then why would the lower CTs have their polarity reversed?
Without a priori information this diagram is difficult to follow. Rich with your information and after I printed out the diagram, then some items were traceable.
.
I put the information for the VS,AS etc in answer to a question as to what they were. It is true that the ct polarity has nothing to do with the switches, but the polarity has a definite relation to the function of the MFM (multifunction meter) which includes, watt, vars, pf, amps, volts, watt-hours, etc, the RS485 is for a scada input for both the MFM and the and the SR750.
The SR750 is a multifunction Feeder Management Relay containing the following functions Phase Timed Overcurrent (51P)
Voltage Restraint
(12 selectable curves plus 2 Flexcurves)
Ground Timed Overcurrent (51N)
Phase & Ground Loset Overcurrent (50PL, 50NL)
Phase & Ground Hiset Overcurrent (50PH, 50NH)
Phase & Ground Directional Control
Zero Sequence (67P)
Negative Sequence (67N)
Negative Sequence Instantaneous (46/50) and Time (46/51)
Overcurrent
Voltage Phase Reversal (47)
Negative Sequence Overvoltage (59Q)
Undervoltage & Overvoltage (27-1, 27-2, 59-1, 59-2)
Underfrequency & Overfrequency (81U-1, 81U-2, 81O-1, 81O-2)
So it serves many functions, which may or may not be used by the user.
The K1 key interlock is designed to allow or prevent the circuit breaker 5-GM1 350 to be opened or closed depending on the arrangement of the circuit breakers on the bus (eg. 2 out of 3 breaker scheme).
The SEL387L is a line current differential relay used for the following:
Protect two-terminal transmission lines and subtransmission lines with the same ratio CTs on each end. Apply a 64 Kb digital communications channel for complete phase and ground fault protection with no settings.
The cts for this relay and their polarities are set for the relationship between the current flow on this end of the feeder and the remote end. It looks at the current flow and converts it to a signal that is proportional to the level and direction at this end and compares it with the signal for the level and direction at the remote end and if it determines that a fault exists on the feeder it opens the circuit breakers at both ends.
The relationship between the polarities between the upper and lower cts has nothing to do with each other, they each serve a different purpose and are used as installed.