Regarding going from CU to AL THHN. Does this make sense?

150A 3P/3W calling for 3 #1/0 & 1#6G CU THHN and 1-1/2" EMT. If going to AL THHN I'd have to use 3/0 and go to 2" EMT?
150A 3P/4W calling for 4#1/0 & 1#6G CU THHN and 2" EMT. If going to AL THHN I'd have to use 3/0 but could keep still use 2" EMT?
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Lastly,

600A 3P/4W calling for 2 sets 4 #350 & 1#1G CU THHN and (2) 3". If going to AL you need #500 but conduit could stay at 3"?

Seem like sometime conduit doesn't need to be upsized when going from CU to AL.
 

kwired

Electron manager
Location
NE Nebraska
I have found AL to always be compact stranded, whether it's THHN or XHHW.
These days it usually is compact, but can't necessarily count on it being compact unless you specifically ask when ordering.

So compact THHN will be smaller than compact XHHW, I think, I know it should be smaller than standard XHHW and nylon outer coating will pull easier than the XLPE does, but XLPE will resist scuffing and other abuse a little better.
 

kwired

Electron manager
Location
NE Nebraska
Lastly,

600A 3P/4W calling for 2 sets 4 #350 & 1#1G CU THHN and (2) 3". If going to AL you need #500 but conduit could stay at 3"?

Seem like sometime conduit doesn't need to be upsized when going from CU to AL.
The 350's are too large for 2.5" but do not "fill" the 3", there happens to still be enough room for 500's in the 3".
 

AC\DC

Senior Member
Location
Florence,Oregon,Lane
Occupation
EC
Do the areas in table 9 mean nothing, or am I reading them wrong? It wouldn’t be the 1st occurrence.
ON table 5A in my 2020 says if you going off the 500kcmil that Post#2 stated
For compact Aluminum
Approximate Area In2
THHN
500 =.6151

XHHW
500= .6082

Seems your right though without looking I would of though THHN would be less
 