current calculation for 3 phase

Status
Not open for further replies.

dataca

Member
Location
California
Hi all. I've always been confused about current calculations for 3 phase power. I'm sure someone will be able to clear this up for me. I see this equation everywhere: I= volt amps/(voltage* power factor * 1.73)

Suppose I have 120/ 208Y, 3 phase, 4 wire source. I like to put a 800VA load between L1 & N (which is 120v).
My question is, is the current:

I= 800VA /(120V* power factor * 1.73)
or
I= 800VA/(208V* power factor * 1.73)

I guess I don't understand which voltage to use.
Thanks for your time.
 
Hi all. I've always been confused about current calculations for 3 phase power. I'm sure someone will be able to clear this up for me. I see this equation everywhere: I= volt amps/(voltage* power factor * 1.73)

Suppose I have 120/ 208Y, 3 phase, 4 wire source. I like to put a 800VA load between L1 & N (which is 120v).
My question is, is the current:

I= 800VA /(120V* power factor * 1.73)
or
I= 800VA/(208V* power factor * 1.73)

I guess I don't understand which voltage to use.
Thanks for your time.
Line to neutral load, as you note, is single phase. No sqrt(3) factoring.

Also VA is the wrong unit measure: P = E?I?pf ...where P unit is watt.

I = 800W ? 120V ? pf
 
I like to put a 800VA load between L1 & N (which is 120v).
That is a single phase circuit. The factor of 1.732 (i.e., the square root of 3) never comes into play for a single phase circuit. For a three phase circuit, that factor is going to show up somewhere along the line. The thing that you need to learn is where to put that factor within any given equation.
My question is, is the current:
I= 800VA /(120V* power factor * 1.73)
or
I= 800VA/(208V* power factor * 1.73)
Both are wrong, for two separate reasons. The first is wrong because, as I said before, the 1.732 does not show up in a single phase circuit. Both are wrong because when going from a value of VA to a value of current, you do not bring the power factor into the equation.

  • For a single phase, 120 volt load, I= 800VA /(120V) = 6.7 amps.
  • For a single phase, 208 volt load, I= 800VA /(208V) = 3.8 amps.
  • For a three phase load, I= 800VA/(208V* 1.73) = 2.2 amps.
 
Line to neutral load, as you note, is single phase. No sqrt(3) factoring.

Also VA is the wrong unit measure: P = E?I?pf ...where P unit is watt.

I = 800W ? 120V ? pf

Actually, if the OP really does mean VA the calculation is just 800/120.
 
Actually, if the OP really does mean VA the calculation is just 800/120.
Good of you to reply.
It's not altogether unusual to have someone pose a question as their first and only post then disappear back into the woodwork.

I see it here and elsewhere.
It's rude.
 