On all two wire 120 v circuits, not on MWBC's.When is a netural considered a current carring conductor on a single phase system 120v / 240v
What about a three wire cable with two switch legs and a neutral?
I have no idea what you mean by "diversity calculations." Also, I don't see anything in the 2008 or 2011 that would have required them, or required an engineer to do them. Can you explain what you meant?First, I learned something new today. The NEC 310.15B no longer requires an Engineer to do diversity calculations.
As I often do, I must be missing something. In the example of the OP, when would it NOT be a CCC?
:?
As I often do, I must be missing something. In the example of the OP, when would it NOT be a CCC?
:?
I have no idea what you mean by "diversity calculations." Also, I don't see anything in the 2008 or 2011 that would have required them, or required an engineer to do them. Can you explain what you meant?
I am going to stick my neck out, and go completely against the flow here .... and assert that a neutral is ALWAYS counted as a current-carrying conductor- even if it only rarely carries incidental amounts of current.
I say this, first, because the distinction only matters when we are talking about derating conductors. Specifically, when the 'current carrying' wire count exceeds three. Let's look at an example to understand the situation ....
Assume a pipe has two circuits in it. We'll do it once as a MWBC, and once as separate neutrals.
As an MWBC, you've already reduced your wire count by 'sharing' the neutral. That neutral can carry as much as half the combined rating of the 'hots.' There's no doubt that it's carrying the full current at least some of the time. In any event, this 'shared' neutral isn't going to affect the derating calculation, counted or not, as the derating starts at four conductors.
As separate neutrals, we have both neutrals carrying the full amount of current all the time. If anything, this will result in additional heating - now, isn't that a contradiction: more copper = more resistance! So, adding that fourth wire kicks in the requirement to derate.
Compare this to the role of the ground wire, which carrys current only when something goes wrong. Ordinarily, it only takes up space - so we count it for wire fill, but not for heating derating.
310.15 B 4 says that a neutral conductor that carries only the unbalanced current from other conductors of the same circuit need not be counted? if this is not a branch circuit with a neutral then what is it? For example if we pull four 20 amp circuits each with their own neutral is that 4 ccc's or 8? It makes a big difference when you get to the derating. Any inspectors out there have an opinion? I assume that since this is in the code there must be a situation where the neutral is not considered a ccc otherwise the code would just say that it is a ccc 100% of the time.
No disrespect to the inspectors but, why would it matter what their opinion may be, it is spelled out in the NEC and the laws of physics, you would follow that.310.15 B 4 says that a neutral conductor that carries only the unbalanced current from other conductors of the same circuit need not be counted? if this is not a branch circuit with a neutral then what is it? For example if we pull four 20 amp circuits each with their own neutral is that 4 ccc's or 8? It makes a big difference when you get to the derating. Any inspectors out there have an opinion? I assume that since this is in the code there must be a situation where the neutral is not considered a ccc otherwise the code would just say that it is a ccc 100% of the time.