The following is from Mike Holt's newletter email dated 7/9/4:
Am I missing something here? Why would you have 4 current carrying conductors for a 2000A feeder. Only thing I can think of is the non-linear load issue mentioned in 310.15.B.4.c.Q 2. If I am using four 500 THHN kcmil conductors in each raceway (all current carrying), how many parallel runs would be required for a 2000A feeder?
A 2. The installation of four current carrying conductors in a raceway requires the use of an ampacity adjustment factor of 80% per Table 310.15(B)(2)(a). The 90?C ampacity of 500 kcmil copper is 430 amperes. The adjusted ampacity for 500 THHN is 430A x 0.80 = 344A. This installation will require the use of six sets of 500kcmil for a 2000A circuit (2,000A/344A).