I am about to start a remodel in a hospital and I'm wondering how many current carrying conductors can I have in a 3/4" pipe? I know that 9 is the "magic number" in normal cases but I was told that the number is different in health care facility.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Are you talking about an Isolated Power System?

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
There is nothing changing numbers of conductors allowed in a raceway, however you should read through 517.30(C).