If retrofitting you end up with less load on conductors than you had before.Now what happens when the load is LED lights?
Lighting and retrofits demand the same load calculation for industrial, construction, maintenance, and service industries,
If designing new, you can light up more area to same light level per circuit than with other light sources.
We are talking about conductor ampacity and overcurrent protection here not load efficiency.
Such load calculation is for general lighting and art 220 calculations. It usually will still be divided into multiple branch circuits that may be 15, 20, 30 or even 50 amp circuits in some cases, which you will apply the conductor ampacity and overcurrent protection rules to each circuit used.