ibew441dc said:
(In between two 3-ways , If I run two travelers, a grounded conductor, and an EGC,)
How many current carrying conductors do I have to apply an adjustment factor to?
Originally my brain had me thinking only two current carrying conductors , because only one of the travelers will be carrying current at a time.
But I am not totally confident with my thinking after studying 310.15.
Any thoughts or input?
Ibew441dc
The real motive behind my original post is based on a problem I ran across at work. (try to bare with my description, I wish I had a picture)
Picture a room that is about 175' long and 50'wide, with 3 entrances (one on each long end and one in the middle on one side)
Original design called for 3 circuits(2,4,6) , each with a 3way at end , 4way in middle , and 3way at the other end (simple enough right.)
Originally I ran a 3/4'' EMT between switches( more than adequate to handle 3 sets of travelers, 1 grounded conductor, and 1 EGC. (all are12 awg and total 8 conductors) (no problem so far and derating is no problem)
Now the problem. The owner decided last minute to make it a/b switching for each circuit (and running additional raceway is very difficult task).
For those who can keep up , you can see my problem.
This doubles the number of travelers I need. The conduit is still large enough (less than 40%) , but if I have to consider each of the travelers as a seperate current carrying conductor my wire is not big enough due to the rules in 310.15.
Infinity hits the nail on the head,(there is no exception)
I'm educated enough in electrical theory to sell the inspector on the fact that only 1 conductor will be carrying current at a time (thus totaling the number of CCC to 7), but I take pride in installing code compliant installations.If I am to consider each as seperate ccc there is 13.
What would yo do?
Thanks
Ibew441dc