Re: Current in Paralleled Conductors
Charlie, you wrote:
quote:
--------------------------------------------------------------------------------
Originally posted by john m. caloggero: There is no problem with the arrangement as described, until the load is increased to the ampere rating of the smallest conductor.
--------------------------------------------------------------------------------
Please allow me to clarify: I infer that you mean there is no physics problem. We all know that it still violates 310.4. Once in a while, as we get off into discussing these strange situations, we need to remind ourselves that academic discussions, design considerations, and code issues are distinct subjects.
Charlie, question: It looks like the #1 was feed to a piece of equipment and the 1/0 wire was feed to another piece of equipment off this 225 amp breaker. Let's say that at the 225 amp breaker, they had the correct type of lugs installed for the #1 & 1/0 wire. Now where each wire ended up at they had and breaker or disconnect with it being fused for that wire size or load. Would this now be a violation? I know we see this type of hook up a lot if you think about it. Say we have a 200 amp disconnect off the meter. From there we might sub off to 2 different panels. Is this the same process like above topic? Just thinking about it.
Thanks!
Jim