I found many threads about current limiting fuses, but not for this specific case. Most of what I can find on the current limiting fuse topic involves trying to protect panels or series ratings with CBs.
In our case, we have a Chiller with SCCR of 5000. and an available fault current at 9800, it has been suggested by more than one person/company, that we can solve with with a current limiting fuse (they showed me it would work using the up, over, down method with the fuse they picked). Question 1) Can you utilize current limiting fuses to lower the available fault current at the equipment? Question 2) If we add a CB at the chiller that is series rated (at 10k or higher)with an upstream fuse at the panel, does the chiller see the advantage of
I know we can lower the available fault current with a lot of extra cable (not feasible here) or by adding a 480v-480v transformer.
Question 3)If we can't use the solutions of questions 1 and 2, which have already been brought up in meetings, how do I explain to the average person (owner/maintenance person) why we can't use those solutions and justify the added cost? Is there a clear code reference or other documentation I can point them to?
In our case, we have a Chiller with SCCR of 5000. and an available fault current at 9800, it has been suggested by more than one person/company, that we can solve with with a current limiting fuse (they showed me it would work using the up, over, down method with the fuse they picked). Question 1) Can you utilize current limiting fuses to lower the available fault current at the equipment? Question 2) If we add a CB at the chiller that is series rated (at 10k or higher)with an upstream fuse at the panel, does the chiller see the advantage of
I know we can lower the available fault current with a lot of extra cable (not feasible here) or by adding a 480v-480v transformer.
Question 3)If we can't use the solutions of questions 1 and 2, which have already been brought up in meetings, how do I explain to the average person (owner/maintenance person) why we can't use those solutions and justify the added cost? Is there a clear code reference or other documentation I can point them to?