I come from the commercial/residential electrical field, but was recently presented with an industrial problem. I'm hoping someone here can give their 2 cents on it.
I have a client that has (60) -- 1200w computers, that require 240 VAC.
Currently, at the location, there is a 3 Phase, 240VAC, 2000A dead front end switchgear service, with several 200 and 400 amp breakers (not used by anything) I believe it is a 240V 3 phase bastard leg system.
What is the safest way, and best way, to power these 60 units?
I calculated so far:
1200w / 240v = 5A / unit
5A / 0.80(%) continuous load = 6.25 A
the 60 units will be placed onto a rack that holds 30 units each.
This gives us 187.5A / rack of 240V requirements.
There were a couple of options I was considering....
OPTION A)
Ignoring the 3 phase, and using just the center tapped legs...
Taking a 400A breaker off of the 2000A servie
Bringing it to a box and bugging off to (2) 200A disconnects...
each disconnect would go with SE cable to a 200A main lug SqD QO box w (10) 2 pole, 20A breakers...
every 3 devices would be connected to a 20A breaker.
* is this more expensive if I'm pulling on only two sides of the 3 phase system?
OPTION B) using a 3 phase SqD QO-B panel -- with a phase balanced load, of 3 machines per 20 A breaker....
* Is this proper?
OPTION C) using DIN rail mounted 60A breakers per 10 machines, and 10 wires going to C-13 endes for each 10 machines of 1200w each
*DOES THIS PROVIDE ADEQUATE LOAD PROTECTION IF ALL 10 machines are always running???
ANY thoughts would be appreciated.
Customer wants to have 60 machines powered by December 31st... 300 machines by feburary 31st (2000A @240V 1 phase)... and 1000 machines by August 31, 2018 (6000A @ 240v 1 phase or 2000A @240V/3phase)
I come from the commercial/residential electrical field, but was recently presented with an industrial problem. I'm hoping someone here can give their 2 cents on it.
I have a client that has (60) -- 1200w computers, that require 240 VAC.
Currently, at the location, there is a 3 Phase, 240VAC, 2000A dead front end switchgear service, with several 200 and 400 amp breakers (not used by anything) I believe it is a 240V 3 phase bastard leg system.
What is the safest way, and best way, to power these 60 units?
I calculated so far:
1200w / 240v = 5A / unit
5A / 0.80(%) continuous load = 6.25 A
the 60 units will be placed onto a rack that holds 30 units each.
This gives us 187.5A / rack of 240V requirements.
There were a couple of options I was considering....
OPTION A)
Ignoring the 3 phase, and using just the center tapped legs...
Taking a 400A breaker off of the 2000A servie
Bringing it to a box and bugging off to (2) 200A disconnects...
each disconnect would go with SE cable to a 200A main lug SqD QO box w (10) 2 pole, 20A breakers...
every 3 devices would be connected to a 20A breaker.
* is this more expensive if I'm pulling on only two sides of the 3 phase system?
OPTION B) using a 3 phase SqD QO-B panel -- with a phase balanced load, of 3 machines per 20 A breaker....
* Is this proper?
OPTION C) using DIN rail mounted 60A breakers per 10 machines, and 10 wires going to C-13 endes for each 10 machines of 1200w each
*DOES THIS PROVIDE ADEQUATE LOAD PROTECTION IF ALL 10 machines are always running???
ANY thoughts would be appreciated.
Customer wants to have 60 machines powered by December 31st... 300 machines by feburary 31st (2000A @240V 1 phase)... and 1000 machines by August 31, 2018 (6000A @ 240v 1 phase or 2000A @240V/3phase)