"Dumping" the main will not clear PoCo as a contributor. You need to isolate the neutral (from the service) as well as the grounded conductors, then you can rule out PoCo.
You may find no change in the current on the GEC when you open the mains and a lowering or vanished current when you lift the grounded conductors.
You may find no change in the current on the GEC when you open the mains and a lowering or vanished current when you lift the grounded conductors.