Ken9876
Senior Member
- Location
- Jersey Shore
I have a situation, there is a 50kva 277 pri 120/240 sec transformer feeding a panel at this location. I noticed when I had the panel cover off to correct a 30amp load on a 20 amp breaker that the neutral was connected to the EG bar in the panel, so I put a meter on it and had 7 amps on this 6 awg jumper. So I took a look at the transformer and the main bonding jumper was installed there, with the GEC. I checked the current on the EGC back to the transformer and had about 3.5 amps. I removed the incorrect jumper at the panel, and the current on the EGC dropped down, but I still have .6-.4 amps on the EGC and on the metal raceways back to the transformer. Is a small amount of current on the EGC normal? and if so what is ok. The loads on this panel vary from lighting and recs. to a UPS for a PLC system and heating and A/C loads, fire alarm...Should I turn off loads untill the current goes away?
Thanks,
Ken
Thanks,
Ken