mikejs
Member
- Location
- gettsburg PA
I have a 3 phase 480/277v 4000a service with a 1200a refrigeration sub-panel that is monitored by the refrigeration company and they are getting a current reading on the grounding conductor, it was as high as 30a but I did some checking and we found the generator had a bounding jumper and our transfer switch was a 3 pole. Once we removed the jumper we were getting around 12a. Our voltage to neutral varies from L1-N 270v, L2-N 277v, L3-N 283v, L1-L2 475v, L2-L3 483v, L3-L1 481v. This is in a 400,000 sqft newly constructed freezer/dry warehouse. I would appreciate any feed-back