Current on Service Raceway
What is the source of that comment? The code clearly permits the use of the neutral for all required bonding and grounding within and on the line side of the service equipment enclosure and that will always result in a parallel path for neutral current where the service conductors are in a metal raceway.
Somehow, I had it in my head that conduits aren't supposed to carry any current, that's all.
This is my only experience where the conduit was used as a neutral. Not quite the resi application under discussion...
That was not caused just by the conduit being in parallel. It was a result of a neutral conductor failure and the conduit was in parallel with the neutral. When the neutral failed the conduit tried to carry the neutral current. This does not happen unless there is an impairment of the neutral.
That's sure speculating a lot by that picture.
That could have been caused by a lightning strike for all we know.
Partial pictures always leave opinions open to speculation.
JAP>
JAP>
Just commenting on what the poster of the picture said. Sure there could be lots of other causes.
Actually, there was no neutral. They used the conduit as a neutral for a pair of 4WD panel feeders. That fault occurred on the line side of that fused switch, so the fuse never blew. Unoccupied building with a bitcoin mine running flat out. The line-side fault heated up the service drop cables enough that they ignited. When the neighbors saw that on fire, the fire co and poco came and put a stop to all the nonsense with a pair of loppers.
Not following the description.
I strongly suspect there was a connection failure that may have eventually led to ground fault.
A feeder would not necessarily require a neutral and an EMT, GRC or IMC is entirely acceptable as an EG when properly installed.
A SE would require a grounded conductor brought to it.
An amateur electrician connected a bunch of branch circuit neutrals to the ground busses in two panels that had no neutral conductors in their feeders, just the conduit as a ground.