I believe it. I was joking a bit with a couple thousand feet, but started to think it's realistically several hundred.
Crunching the numbers I keep running into the same thing. Maybe I'm doing something run, however at the same time the whole 250% OCPD rule doesn't feel right. At least not without some type of run lenghth restriction in the code.
I'm thinking
So I did find this:
en.wikipedia.org
According to the graph #12 can only handle 235 amps for in 10 seconds.
However at 235 amps a 40 amp THQL breaker takes upwards of about 10 seconds to open.
Reading up on Kohler specs it seems that a typical generator delivers about 300% its rated current for 10 seconds.
So, 235 / 3 = 78 amps, times 208 x 1.73= 28 kw. So in theory any generator under 30kw would automatically not provide enough short circuit current for rapid opening...? Hhmmm