Current Transformer Neutral Bonding

Status
Not open for further replies.

dumontm

New member
IEEE Std 141-1993 11.8.1 Current Transformers 4th paragraph states:

"Current transformers must have a secondary circuit ground at one point when they are required to be grounded. The National Electrical Code (NEC), ANSI/NFPA 70-1993 [B5], Section 250-L, specifes minimum grounding requirements for instrument transformers. The ground will establish a firm ground reference point and will restrict the buildup of static voltages caused by the high-voltage conductor(s)."

I am unable to locate Section 250-L in the 2005 NEC, the only copy I have access to.

Can someone summarize what the section intends? Is it common to ground the neutral conductors of a 3-phase CT arrangement for safety reasons? What situations would make it legitimate to leave it ungrounded.

Our particular arrangement was feeding information into a genset control panel and the manufacturer's info suggested grounding was optional. Unfortunately as I write this I no longer have a copy of the manual in front of me (it is at site) and cannot recall if there were criteria attached the the "optional" statement.

This is for a Canadian installation and I cannot locate any specific reference in the Canadian code for such installations. It appears it was also removed from the NEC but I am wondering what was there and why, and why it was removed.

Regards,
Mark Dumont
Calgary, Alberta
 
Mark,
Your reference is to the 1993 NEC. Article 250 was reorganized in 1999. What was Section L in the 93 code is section IX in the 2005 code. 250.170.
Don
 