I have a client that has installed custom permanent furniture in their office. Internally they snaked Wires through the various tiers & installed Table lamps(4 looped together ) with zip cord & are plugged into a receptacle I installed underneath.
I’m looking at 400.8 to convince the client that this is against code, but because it only mentions structure , ceilings & walls they don’t seem to think it applies.
is there any other code sections that I should be looking at.