eljefetaco
Member
- Location
- Fanwood, NJ
I am going to keep it brief until I see a few responses. (Obviously requiring me to do more fact checking) I have been brought into a job where the customer is getting an electrical shock when they touch the shower faucet. Previously it was a plastic faucet. If you take electrical meter from cold water to ground no voltage. (Or Hot water, heater is bonded). Go cold water to floor tile on I get 8 volts only when floor is wet. . If I turn the floor tile heater on I Get 64 volts. I have completely ruled out the tile floor heater as it was disconnected during my testing and only made matters worse. I suspect a bad neutral somewhere. The utility came out and said all good on there end. I put my amp meter on grounding electrode to water meter and get 1.2 amps. The Neutral from meter to incoming service is carrying a load also. Not Sure if current is coming in or going out. Have narrowed it down to a possible three circuits in the house. If I turn them off no current on water pipe. Crazy. Any thought??