Is the floor a grounded surface? By that I mean is it tile on a wood subfloor or tile on concrete on grade?
If it is a grounded floor you very well may just be measuring voltage drop on the service neutral, or even voltage drop on the POCO MGN being extended to you on the service neutral. Your floor is at true ground potential in this case and your electrical system grounded/grounding conductors are at some point above ground.
Seen this same thing happen before in older home with metal sewer piping still run into the ground and it wasn't bonded to the electrical system. Cold water pipe was bonded to electrical system and you would get a shock in the tub because of voltage between water supply piping and waste piping.
Measure voltage between service grounded conductor and a probe out in the yard. If you have more then 5 volts your problem is likely outside the house, even 5 volts is probably a little high but any more then that is a pretty serious stray voltage issue.
If it is a grounded floor you very well may just be measuring voltage drop on the service neutral, or even voltage drop on the POCO MGN being extended to you on the service neutral. Your floor is at true ground potential in this case and your electrical system grounded/grounding conductors are at some point above ground.
Seen this same thing happen before in older home with metal sewer piping still run into the ground and it wasn't bonded to the electrical system. Cold water pipe was bonded to electrical system and you would get a shock in the tub because of voltage between water supply piping and waste piping.
Measure voltage between service grounded conductor and a probe out in the yard. If you have more then 5 volts your problem is likely outside the house, even 5 volts is probably a little high but any more then that is a pretty serious stray voltage issue.