Customer wants a 20amp circuit in bedroom for a microwave

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
The panel is zinsco (thanks guys) so since they don't make AFCI zinsco breakers, is it ok to use a non-AFCI breaker? Do they make AFCI outlets yet? Thank you for your help.
 

danickstr

Senior Member
i think they do make cafci outlets. Don't get just an afci, they no longer are good for 2008

but the home run has to be in a metal jacket (emt, a/c) not sure if flex works.
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
time to put on your "salesman" hat & explain to the homeowner the Zinsco risk & replacement breaker cost. If that fails, it sub-panel time
 

danickstr

Senior Member
combination afci for both series and parallel shorts, i think

but I agree that a Zinsco panel is not something they should want to keep, if they can afford it.
 

480sparky

Senior Member
Location
Iowegia
What's wrong with a bedroom mini-bar?



ra30.jpg



Why not install a regular breaker, and use that circuit to feed a 2-circuit subpanel? Install an AFCI there.
 