A service entrance cable with three 4 AWG Copper conductors was chosen by the electrical contractor to replace the original service entrance cable at a single-family dwelling. When making the inspection, I noticed that the old split-bus Federal Pacific NoArk Service panel was rated 125 amps.
2005 NEC 230.42(A) states, in part, that the ampacity of the service entrance conductors be determined from 310.15.
Table 310.15(B)(6) lists the conductor type and size for a 125 amp service to be 2 AWG Copper.
Must I require the contractor to upsize the service entrance cable or downsize the service panel or is the use of 4 AWG copper supplying a 125 amp-rated panel allowed somewhere in the NEC.
Thanks