I'm too lazy to do the math on this right now, but I suspect the above statement is only true if the 'high power supply lines' were low enough to bump your head on.
i've actually measured some pretty significant voltages induced
in a 230 kv switchrack.... the bus was about 35' overhead, and a
10' stick of pipe, in the afternoon when the AC load was at a peak,
could get a measured 80+ volts on 10' of pipe. that sounds nuts,
but i measured it with a fluke 12, with my own hands. i asked one
of the station operators about it, and he said that bus peaked at
over 2,000 amps of 230kv in mid afternoon....
it wasn't a static charge either.... you could spin a drill motor with it.
we got curious when we noticed you'd get shocked touching the
work truck without gloves in the afternoon, but not in the morning.
as for this "wonder invention"? sounds like doing nothing is what it
does best.....
randy