USE IN FIRE RATED ASSEMBLIES
Listed single- and double-gang metallic outlet and switch boxes with
metallic or nonmetallic cover plates may be used in bearing and nonbearing
wood stud and steel stud walls with rating not exceeding 2 h. These walls
have gypsum wallboard facings similar to those shown in Design Nos.
U301, U411 and U425, as covered under Fire Resistance Ratings ? ANSI/UL
263 (BXUV). The boxes are intended to be fastened to the studs with the openings in the wallboard facing cut so that the clearance between the
boxes and the wallboard do not exceed 1/8 in. The boxes are intended to be
installed so that the surface area of individual boxes do not exceed 16 sq in,
and the aggregate surface area of the boxes do not exceed 100 sq in per 100
sq ft of wall surface.