I recently saw a question in Electrical Contractor Magazine (bottom of page) and was surprised at the answer given.
http://www.ecmag.com/index.cfm?fa=article&articleID=9380
The question involved an appliance with a 15 amp attachment plug, a nameplate rating of 13.6 amps and a 15 amp branch circuit. The answer given said that the attachment plug must be removed and changed to a 20 amp on a 20 amp circuit. Since when does the NEC require us to rewire listed equipment?