what is the max distance from fixture that mc can be unsuported or fastened? Code number if you can.
Last edited:
mdshunk said:You could have some MC cable installed in a building 100 miles from a given fixture.
Jim W in Tampa said:what is the max distance from fixture that mc can be ? Code number if you can.
They are lay in 2x4.Have a guy saying it must get strapped within 12 inches i think he nuts but figured i might missed somethingnakulak said:330.30 C and D, see exception where fished (2005)
Jim W in Tampa said:They are lay in 2x4.Have a guy saying it must get strapped within 12 inches i think he nuts but figured i might missed something
BackInTheHabit said:The 12" refers to romex going into boxes as per 2008 NEC 334.30.
NEC 330.30 (D)(2)
"....For the purpose of this section, Type MC cable fittings shall be permitted as a means of cable support.
georgestolz said:In the case of prefab luminaire whips, does there need to be a support within 12" of the box before the 2x4 (i.e. does the whip have to be supported at the 4 square?
Jim W in Tampa said:Ok let me fix question.How far can i be without fastening
Jim W in Tampa said:what is the max distance from fixture that mc can be unsuported or fastened? Code number if you can.
Jim W in Tampa said:No you let him fall flat on his face.If he he doesnt know what he needs then send him home.That guy has got to be a joke,he is asking $10 hour guy to do journeymans work.
I believe it is when fished... No support at all...POWER_PIG said:I wonder why an MC connector is considered good enough to be a means of support in an accesible ceiling (not exceeding 6' respectively) and not in wall?
Yes, good call. I suppose it would create a problem if all your MC's are flappin' in the wind by the connectors while the drywall is going up.e57 said:I believe it is when fished... No support at all...