daisy-chain 2x4 lay-ins

Status
Not open for further replies.

prs1029

New member
I know we use to be able to daisy chain 2x4 lay ins in 300.15. But I heard rumer that this was no longer acceptable. Is this true or are they making up codes again?
 
'08 ~ 410.64; 410.65
'05 ~ 410.31; 410.32
'02 ~ 410.31; 410.32
'99 ~ 410.31

No more rumors ;)
 
.....I got lazy ....I don't have those years on the computer :smile:

This help?

2008Augcodecollectionlabelssmall.jpg
 
I know we use to be able to daisy chain 2x4 lay ins in 300.15. But I heard rumer that this was no longer acceptable. Is this true or are they making up codes again?

Definitely a made up code.

However, I think regional practices may have something do with this rumor. I know that in other parts of the country it's very common to run an EMT with a j-box to each light location and then run a whip down to each light.

Here in New England we almost always daisy chain with MC cable unless it's spec'ed otherwise.
 
We see quite a few daisy chains using the 18 ga whips that come with the fixture and of course that is not allowed.
240.5(B)(2) permits the use of #18 fixture wire in lengths up to 50' to be protected by a 20A OCPD. If the total wire length of the conductors in the whips is 50' or less, the code would permit daisy chaining.
 