I know we use to be able to daisy chain 2x4 lay ins in 300.15. But I heard rumer that this was no longer acceptable. Is this true or are they making up codes again?
Not to my knowledge but take a peek at 410.130(G)
That's the requirement for the discos in each fixture... nothing to do with daisy-chaining.
'08 ~ 410.64; 410.65
'05 ~ 410.31; 410.32
'02 ~ 410.31; 410.32
'99 ~ 410.31
No more rumors![]()
'08 ~ 410.64; 410.65
'05 ~ 410.31; 410.32
'02 ~ 410.31; 410.32
'99 ~ 410.31
No more rumors![]()
Well said Celt.
That's it? No '96, '93, '90.....???![]()
.....I got lazy ....I don't have those years on the computer :smile:
ins Is this true or are they making up codes again?
This help?
I know we use to be able to daisy chain 2x4 lay ins in 300.15. But I heard rumer that this was no longer acceptable. Is this true or are they making up codes again?
This help?
![]()
This help?
![]()
Man, you've been an electrician for a long time.:smile:
240.5(B)(2) permits the use of #18 fixture wire in lengths up to 50' to be protected by a 20A OCPD. If the total wire length of the conductors in the whips is 50' or less, the code would permit daisy chaining.We see quite a few daisy chains using the 18 ga whips that come with the fixture and of course that is not allowed.