I'm currently building a Storage Unit in FL. We have hundreds of 4' Strip fixtures mounted directly to the ceiling. The fixtures are allowed to be end to end. We installed MC cable in one end of the fixture and out the other to the next light. They are separated by about 5'. Since there are EM Strip Fixtures, every other fixture, we are running 12/3 MC through each fixture for the EM Batteries. At some points we are coming out of the strip fixtures and feeding an exit sign with a 12/2 Whip.
We just had inspection and the inspector is quoting NEC 410.64 - We are not allowed to use the fixtures as a raceway. Saying we are not allowed to go in one end and out the other, he is also saying we are not allowed to feed the exit sign from another fixture.
My fixtures specifically say they are allowed to be end to end which would allow what we are doing from exception "C" of 410.64 as it specifically says "connected together by approved wiring methods"
Also NEC Section 300.15B allows luminaires to act in lie of boxes as long as they have a J-Box or Wiring compartment.
Anyone have any ideas on how to counter this? or am I completely wrong in this?
We just had inspection and the inspector is quoting NEC 410.64 - We are not allowed to use the fixtures as a raceway. Saying we are not allowed to go in one end and out the other, he is also saying we are not allowed to feed the exit sign from another fixture.
My fixtures specifically say they are allowed to be end to end which would allow what we are doing from exception "C" of 410.64 as it specifically says "connected together by approved wiring methods"
Also NEC Section 300.15B allows luminaires to act in lie of boxes as long as they have a J-Box or Wiring compartment.
Anyone have any ideas on how to counter this? or am I completely wrong in this?