Project we are doing down in St. John USVI, The excavator/GC damaged the existing 600 ampere feeder conduit that was on premises.
The existing 120/240 single phase feeder was piped/installed(not by us) with 3 sets of 3/0 in 1 X 4" PVC conduit fused @ 600 Amps @ 250 feet. The damage was done on 1 of the sets on the phase side.
We are discussing options for repairs and I would like to hear from some other professionals.
My first option was:
A couple of points on option 1/2: I'm up sizing to the 500 mcm to accommodate for the length of run and lower the voltage drop.
The last option which I told contractor I advised against and wouldn't do is:
I've attached some pics.
Thanking you guys in advance.



First time posting but life long viewer and supporter of MH and site.
Project we are doing down in St. John USVI, The excavator/GC damaged the existing 600 ampere feeder conduit that was on premises.
The existing 120/240 single phase feeder was piped/installed(not by us) with 3 sets of 3/0 in 1 X 4" PVC conduit fused @ 600 Amps @ 250 feet. The damage was done on 1 of the sets on the phase side.
We are discussing options for repairs and I would like to hear from some other professionals.
My first option was:
- Shunt out the damaged conduit allowing us to work and open trench as necessary. We can then remove and abandon old conduit and feeders. Re pipe 2 X new 3 or 4 inch PVC conduits. Install 2 new sets of 500 Mcm feeders.
- Shunt out the damaged conduit. Remove damaged section of conduit/feeder. Try and remove the existing 3/0 feeder. Repair existing 4 inch conduit as needed. Pull 2 new sets of 500 mcm in existing 4 inch conduit. I'm concerned with the integrity or this conduit and not sure if its been damaged anywhere else. Plus the pull will be a bear.
- Cut back on shorter section of feeder. Have GC install property box. Re pipe into a proper splice box. Pull new sets of 3/0 cable on the shorter side and splice accordingly.
A couple of points on option 1/2: I'm up sizing to the 500 mcm to accommodate for the length of run and lower the voltage drop.
The last option which I told contractor I advised against and wouldn't do is:
- The contractor wants to do a direct burial splice on the cable and try and rebuild the conduit using resin, pipe etc. I'm totally against this as the THWN/XHHW wires inside damaged conduit are not listed for direct burial.
I've attached some pics.
Thanking you guys in advance.