Hi guys I need help I installed a new Nema 3R Disconnect and a Nema 3R Panel next to a existing Nema 3R meter panel. We used the bottom KO's which are about 3" from the bottom of each enclosure to connect from the meter section to the disconnect to the panelwe used 2 1/2" thru thread and had a lock nut on each side. we also had a few penetrations from the top of the panel and used Myers hubs. My inspector is telling us that we need to put myers hubs on the penetrations on between the panel disconnect and meter section. I asked this last week and someone gave me this :
312.2 Damp, Wet, or Hazardous (Classified) Locations
(A) Damp and Wet Locations In damp or wet locations, surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least 6-mm ( 1/ 4-in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof. For enclosures in wet locations, raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations.
I found this code but cannot find the part that talks about if we come in above the level where there are unisulated parts that we need to use a wet location fitting.
If im made to chage to myers hubs I will basically have to redo all the work.
I have never had an issue but now I have to present it to the inspector and I need the code thats talks about the area you enter below uninsulated parts.
Please Help !!!!
312.2 Damp, Wet, or Hazardous (Classified) Locations
(A) Damp and Wet Locations In damp or wet locations, surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least 6-mm ( 1/ 4-in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof. For enclosures in wet locations, raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations.
I found this code but cannot find the part that talks about if we come in above the level where there are unisulated parts that we need to use a wet location fitting.
If im made to chage to myers hubs I will basically have to redo all the work.
I have never had an issue but now I have to present it to the inspector and I need the code thats talks about the area you enter below uninsulated parts.
Please Help !!!!