Hello all!
During commissioning of a switch panel, thermistor input on one of the MCD500 softstarters was short-circuited. Now it displays "thermistor trip" permanently. Is there a way to reset it or the unit is damaged permanently?
Jraef
Electrical Engineer
Connect a wire between the thermistor input terminals on the starter. Thermistor circuits work by looking for the resistance to increase, which can also mean an open circuit. So by putting a jumper wire between the terminals, you are emulating a low resistance circuit, which should be interpreted by the trip unit as a cold thermistor; good to go If it still displays “Tripped”, the circuit is damaged internally and is unlikely repairable without replacing whatever control board it is in.
Anton.N
NL
Thanks for the reply.
I connected a 100ohm resistor to thermistor input and then I was able to reset "thermistor trip" error. So probably the measuring circuit is intact. But when I disconnect thermistor input, I still get the same error. The other softstarters in this panel have exact same settings, but they don't trip when thermistor is diconnected.