Plant owner called me today, and said somebody cut the uffer rebar off flush with the slab on the new building, and wanted to know what to do! Looks like I will have to break out the coring bit, he doesn’t want the concrete jacked up around it!
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Drive Rods?
We never get to use an ufer up here. Someone always doing something similar.
The problem with that approach is that unless there is a local amendment to 250.50 the CEE has to be used because it is present.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Yes it's present, maybe not accessible or available but it is present. NC did the right thing and amended it to say accessible, but the NEC hasn't.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Yes it's present, maybe not accessible or available but it is present. NC did the right thing and amended it to say accessible, but the NEC hasn't.
This argument make the exception invalid as almost without exception the rebar in the footer will qualify because of how it's tied. Exception: "not accessible for use without disturbing the concrete."
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
This argument make the exception invalid as almost without exception the rebar in the footer will qualify because of how it's tied.
The exception is addressing existing buildings.
Exception: Concrete-encased electrodes of existing buildings
or structures shall not be required to be part of the
grounding electrode system where the steel reinforcing bars
or rods are not accessible for use without disturbing the concrete
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Yes it's present, maybe not accessible or available but it is present. NC did the right thing and amended it to say accessible, but the NEC hasn't.
I disagree that this is the right thing. They might as well say "if you feel like it." Or go back to the way it used to be, optional not mandatory.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I disagree that this is the right thing. They might as well say "if you feel like it." Or go back to the way it used to be, optional not mandatory.
Yes, that's basically what it's saying and for no more than it does it's the right call.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Makes me more money! Every time I pull my hammer drill off the truck, it’s $125! Harbor Freight super SDS drill has already paid for itself in less than 6 months!
 

kwired

Electron manager
Location
NE Nebraska
Done, steel guy did not know what it was, and said it was in his way. He apologized for cutting it off.
NEC changed the wording almost 20 years ago to the way it reads now. Was this his first project ever?

I think they did good when changing it. Before the change CEE's were almost never used even if there was qualifying CEE present. Almost every footing is a qualifying CEE. Slab on grade building might be about only time you won't find one, though many those have an actual footing around perimeter anymore. Small utility shed might be where it won't be so common.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
NEC changed the wording almost 20 years ago to the way it reads now. Was this his first project ever?

I think they did good when changing it. Before the change CEE's were almost never used even if there was qualifying CEE present. Almost every footing is a qualifying CEE. Slab on grade building might be about only time you won't find one, though many those have an actual footing around perimeter anymore. Small utility shed might be where it won't be so common.
Until we started getting inspections, I’m probably the only local contractor that put them in. I’ve been putting them in since the 80’s. It is a Walmart spec on their buildings, the service, and every transformer location throughout the building. I even have one on my own house I built in 92’.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Our inspector is looking for it on residential footer inspections, though I don’t know how many electricians know you don’t have to put copper in the slab, that if you can turn it up in a wall that is accessible, you can tie in there. That way you don’t have to worry about the copperheads cutting and stealing your wire.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Yes, but by time the inspector is called, the building "IS" existing. And, I Yet to see one myself.
And if you wait long enough to call for an inspection you can also fish all the wiring using that logic. ;)
 