Lets consider a 2000 amp main installed in a high rise office building. The breakers feeds the upper half of the building via bus duct. The breaker has ground fault protection. It's 9:00am on Monday. Whats your call?????
ghostbusters?
if the breaker in question feeds the bus duct, ya can't megger it without
opening all the bus taps. i'd want to megger it before i blew something, maybe
myself, up.
everyone's gonna scream like a mashed cat at the delay. ok.
they are gonna want in on, NOW. ok.
opening 10 floors of disconnects is gonna take half an hour. best to start at
the top floor, and work your way downward. it's faster that way.
and make sure you have enough locks... everyone is gonna be flipping stuff,
trying to get it back on...
to do it correctly, parts of that building are gonna be off for at least 2 hours.
if the bus is ok, you can start meggering each floor, and turning it back on,
but it's gonna take a while, unless you have a crew helping you. you're gonna
have to turn off all the breakers in each panel, megger the feeders and
bus tap, light it back up, and close all the branch breakers.
if the bus duct is shorted.... well..... you're gonna have a busy day...:smile:
ever try to pull a bad section of bus duct out of the middle of a vertical riser?
even if you had a remote recloser, and were under no danger personally.
do you want your name written all over a huge emergency repair bill?
a guy who was my journeyman in my second year, went to work 15 years
ago for DWP. smart, brilliant at times, he did some really nice work there.
and one day, his crew had removed personal shorts and grounds, at a
powerhouse, and he went to light up a can. the breaker relayed. often times,
some of the equipment in service is old, and problematic. if it's been off for
10 months, like this situation, it'll have to be push started, so to speak, and
so instead of checking, he threw the switch a second time.
someone had added a SECOND set of shorts and grounds, and had tucked
them nicely out of the way, so they were easy to miss. how thoughtful.
repairing the damage was approx. $2M. a black mark in the copy book,
to say the least. thank god nobody was hurt.