- Occupation
- Licensed Electrician
We do, do that if we put a service disconnect right next to the meter or use a breaker panel with a built in meter base.It would be better, yes, but the electric utilization industry isn't always in sync with the electric distribution industry. The utilities insist on bonding their neutrals to their meter enclosures. And the NEC insists that we bond the neutral at the service disconnect. And neither is going to give.
If we could just start our EGC from the meter neutral, then we wouldn't need the MBJ and all of our neutrals would be insulated from ground.
If you substitute a CT cabinet where you are talking about the meter you get power company engineers and local inspectors screwing this up all the time. I have seen an extra green wire pulled from the panel with the MBJ back to the CT can more than once.BUT! There is no NEC requirement for a meter at all. So, Maybe we could insulate the neutral at the meter and use a MBJ at the disconnect and take an EGC back to any meter that might be installed? The utility is NOT going to rely on us to ground their equipment. So we just live with it.