The 2005 NEC in section 410 (F) (5) has a new requirement for HID lamps, other than a thick glass PAR type, to have a barrier that encloses the lamp, or only allow a Type 0 lamp.
A type O lamp has a longer neck, if a non type O lamp is screwed into the socket it won't make contact.
The reason this change was submitted is if an HID lamp is left on 24x7, the HID lamp will not reach its end of life condition where is normally goes out, and the lamp will explode. Several fires have been attritubed to this.
This commerical garage had HID lighting that is on 24 x 7:
One of the HID Lamps exploded:
If you have HID lighting that is on 24x7, you can turn off the luminaires 15 minutes a week, this will allow the lamp to cool off, and when it reaches end of life it will go out and not explode.
A type O lamp has a longer neck, if a non type O lamp is screwed into the socket it won't make contact.
The reason this change was submitted is if an HID lamp is left on 24x7, the HID lamp will not reach its end of life condition where is normally goes out, and the lamp will explode. Several fires have been attritubed to this.
This commerical garage had HID lighting that is on 24 x 7:
One of the HID Lamps exploded:
If you have HID lighting that is on 24x7, you can turn off the luminaires 15 minutes a week, this will allow the lamp to cool off, and when it reaches end of life it will go out and not explode.