I've got a question about circuit loads. We are planning on installing a rack of 12 render nodes (like servers). Hewlett-Packard says that the real world load that each of these servers draws is 1.9 Amps at 208 VAC. We were planning on using a 208 VAC 30 Amp circuit to power all of these servers. My impression of circuit loading was that you could go up to 80% of what the circuit is rated at. Since each of the servers is 1.9 Amps and there are 12 of them, this would put us at 22.8 Amps or 76% of the rated circuit load. The building engineer has taken issue with this purposed setup saying that 76% of the load too close to the 80% specified by the NEC.
I was always under the impression that you could load up to 80%. He seems to be suggesting that 80% is a drop dead max and that you should plan for a lower percentage of circuit use.
What the right answer? What Amperage percentage should be shooting for?
I've got a question about circuit loads. We are planning on installing a rack of 12 render nodes (like servers). Hewlett-Packard says that the real world load that each of these servers draws is 1.9 Amps at 208 VAC. We were planning on using a 208 VAC 30 Amp circuit to power all of these servers. My impression of circuit loading was that you could go up to 80% of what the circuit is rated at. Since each of the servers is 1.9 Amps and there are 12 of them, this would put us at 22.8 Amps or 76% of the rated circuit load. The building engineer has taken issue with this purposed setup saying that 76% of the load too close to the 80% specified by the NEC.
I was always under the impression that you could load up to 80%. He seems to be suggesting that 80% is a drop dead max and that you should plan for a lower percentage of circuit use.
What the right answer? What Amperage percentage should be shooting for?