Dave Dungan
Lmao I am with Larry you guys are just rediculous...
Larry You would never get sensored....:roll:
a bolted fault is when a short circuit bypasses the normal load via a low impedance path that can carry 100's or even 1000's times the current..
Your A typical arcing fault uses a higher impedance path..
Could it be?
Could it be?
I knew an unhandyman once who created a screwed fault.
He screwed black and white to the same side of a receptacle.
Could this be the reason for licensing?
Hey!
Leave Larry alone! He is an end of the line resistor of unknown value(s).
mpross said:
You can have a three phase 'bolted fault', or other types. I take this to mean that there is no impedance to ground.
~Matt
A bolted fault can be L to G, L to L, L to N or L, to L to L, to N to G.
Normally, short circuit studies involve calculating a bolted 3-phase fault condition. This can be characterized as all three phases “bolted” together to create a zero impedance connection. This establishes a “worst case” condition that results in maximum thermal and mechanical stress in the system. From this calculation, other types of fault conditions can be obtained.
To determine the fault current at any point in the system, first draw a one-line diagram showing all of the sources of short-circuit current feeding into the fault, as well as the impedances of the circuit components. To begin the study, the system components, including those of the utility system, are represented as impedances in the diagram.
It must be understood that short circuit calculations are performed without current limiting devices in the system. Calculations are done as though these devices are replaced with copper bars, to determine the maximum “available” short circuit current. This is necessary to project how the system and the current limiting devices will perform.
There are four basic methods for conducting short circuit calculations. These include:
1. The ohmic method
2. The per unit method
3. Computer Software method
4. The point-to-point method
I knew a licensed journeyman who pigtailed ungrounded and grounded to a switch. For the life of him, he could not figure out why the OPD kept tripping.
But seriously, a bolted fault is a term used by folks, and most often associated with discussing or performing fault current calculations. The condition applies to SLG, LL, LLG, and 3phase faults where you assume the impedance between the lines and ground, or between the faulted lines is zero. However, this is an assumption becasue unless you purposely create this condition, all faults have some impedance.
There are multiple reasons for assuming a zero fault impedance. The first is that since every fault condition is unique, it would be physically impossible to know this value in determining fault current levels so it would be arbitray anyway. Second, is that in the calculations this impedance simply reduces the fault current from the maximum possible and therefore if the wrong value was used (to high), it could lead to improperly rated equipment. The real world impedance is typically so small that the reduction would not affect the rating of the equipment, or normally change the level in which you would select a relay to trip. To include it, would mean an arbitrary number is used anyway, and therefore provides no real value in attempting to use it.
On the flip side, every fault has some impedance involved in the faulted connection. If a distribution line goes down over a tree, the impedance is very high, and the relay may not trip, unless other parameters are looked at, and this is why line relays react on other parameters as well.
The difference in fault current and arc flash current is that arc flash calculations include a reduction for the impedance in the fault.
It sounds like a 2-wire switch loop that got mis-wired at the switched-load end.