darunedefig
Member
- Location
- HV, New York
- Occupation
- Electrician
Searching this forum there were some old discussions about AC and DC next to each other. One thread talked about not having an issue with DC spaced 2x depth from AC because, but that was for medium voltage cables and concerning heat flow.
I don't believe there will be an issue with electric magnetic fields if the DC and AC are in separate conduits/cable in the same trench. I don't think there will be an issue if those conduits/cables are horizontal (not vertical) spaced 1" for the full length of the trench run from each other.
Seems the 2023 NEC allows for DC and AC in the same conduit together or at least for solar as per 690.31(B) Exception: Where all conductors or cables have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the same wiring method.
I have a job where there are two existing PVC SCH 40 conduits touching each other in a trench and a customer who is worried about EMF from AC messing up the DC or vice versa. The job is less than 200 amps from both DC 600V and AC 240V and 400' trench run. Does anyone know if there could be an issue?
Also let us say a 200 amps 350kcmil Al direct buried cable is right next to the same size DC cable, would there be an issue?
I don't believe there will be an issue with electric magnetic fields if the DC and AC are in separate conduits/cable in the same trench. I don't think there will be an issue if those conduits/cables are horizontal (not vertical) spaced 1" for the full length of the trench run from each other.
Seems the 2023 NEC allows for DC and AC in the same conduit together or at least for solar as per 690.31(B) Exception: Where all conductors or cables have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the same wiring method.
I have a job where there are two existing PVC SCH 40 conduits touching each other in a trench and a customer who is worried about EMF from AC messing up the DC or vice versa. The job is less than 200 amps from both DC 600V and AC 240V and 400' trench run. Does anyone know if there could be an issue?
Also let us say a 200 amps 350kcmil Al direct buried cable is right next to the same size DC cable, would there be an issue?