Small AB PowerFlex 4, 3 hp IIRC, 480, line reactor, coast to stop, on a conveyor that does not coast. It has ran for 5 years as it is set up with no problems. Last week it shut down when it failed to start after an overvoltage fault. Auto restart is set at 5 times, 1 second apart. We powered it off, reset it and it ran until this morning. Same faults. Then of course no problems the rest of the day
POCO said no voltage problems in the area last week. Larger motors in the facility have PFC capacitors but they do not cycle. Only the 3 hp cycles.
I set the delay between restart attempts to 2 seconds before I left this morning but now I see the manual suggests 0 seconds. ?? Why zero?
Can the VFD be reaching EOL, already? I would not think high buss voltage would be an indicator of that.
Buss voltage was 670 while I was there.
POCO said no voltage problems in the area last week. Larger motors in the facility have PFC capacitors but they do not cycle. Only the 3 hp cycles.
I set the delay between restart attempts to 2 seconds before I left this morning but now I see the manual suggests 0 seconds. ?? Why zero?
Can the VFD be reaching EOL, already? I would not think high buss voltage would be an indicator of that.
Buss voltage was 670 while I was there.