I have an application for DC bussing at 12VDC, 1,000A. A previous installation used three cables 350kcmil THHN. Assuming 90? insulation, we have 1,050A ampacity at 86?F, free air.
There are six cables running 200-300' in Sched. 40 PVC. Derating for 95?C ambient (94%) and 4-6 cables in a conduit (80%), I get a total ampacity of 790A. If using 600kcmil, with derating, the total ampacity would be 1,072A.
Am I right? Do we need 600kcmil? Do the derating requirments apply to DC bussing?