I am sizing the circuit from the combiner box to the inverter. The Isc is 9.24A, and there are 18 strings in parallel. Aluminum conductors are being used. The applicable temp. derate is 0.82.
The SMA inverter I am using is DC 1000V and has the following fuse sizes available:
200A
250A
315A
350A
400A
450A
Typically, I simply take 9.24*1.56*18 = 259A --> 300A fuse. In this case I am left with using a 315A fuse.
My question is: does the derated ampacity of the conductor need to be greater than the standard fuse rating of 300A, or can it simply be greater than 250A? The former pushes the size to 600 kmil, while the latter leaves it at 400 kcmil.
On a side note: Using the ASHRAE 20-yr max. dry-bulb temps leaves the derate at 0.82. Dropping to the 10-yr max. leaves a 0.87 derate, so some engineering judgment needs to happen here as well.