Charlie is right. The OCPD is not to protect the device, it is to protect the conductors to not start a fire.Originally posted by bobhudon:
... I have the conductors protected. My confusion is device protection. If the manufacture does not protect his device from internal shorts/overload then do I have to supply it? ...
The device at some point becomes a fuse- current will pass through some component that will open the path way. What you are trying to do is open a current path and extinguish the arc that results when that occurs. Like a power fuse that can open a high fault current, the device must provide a containment when the catastrophic failure happens.If I size the OCPD to protect the wire feeding power to the device at say 7-amps but the internal wiring of the device can only handle say 1-amp then am I not still leaving the potential of a fire starting if the device malfunctions and continuously draws more than 1-amp?
If this is the case, I'd do both, just like a miniature power distribution setup.Originally posted by bobhudon:
If I have multiple DC loads that each draw a maximum of 80-ma then do I have to fuse each load at 1/10-amp or are the loads allowed to be combined and protected by one fuse?
If we're talking about low voltages, surmising from the 80 ma per device, I don't believe that code really applies.Originally posted by bobhudon:
petersonra,
The branch circuit is being protected by the feeder fuse. Branch circuit wires are sized to handle feeder current. If any branch current or sum of branch currents exceeds feeder fuse rating the fuse will blow. To satisfy code do I also need to add another fuse for each branch?
I realize it is best to fuse each branch for convenience purposes but is it actually required by code in the above scenario? Again, cost reduction is the goal.