Why not use a standard 3-pole disconnect (rated for DC loads of 12 amps which I'm sure would be no big deal) and open only the positive (or negative) leg of each circuit? (If the DC side has a grounded leg, open whichever leg is NOT grounded.)
I see no reason to open both legs of a DC circuit in this case.
Oops, you'd still need two switches for the six inverters. My bad.
How could we possibly know this from the info given?
We can't.
Depending on the load a rotary disconect switch may be what you need.
Bob, when you work on your truck do you disconnect BOTH cables from the battery?
Unless the inverters are connected to the DC side in some sort of series arrangement, interrupting one lead from the DC will adequately disconnect them from the PV panels.
And for single phase circuits, do you open the neutral to work on it? Same principle IMHO.
I do agree that full info wasn't given , but c'mon this is not rocket science. :grin:
I could parellel them but I have to have six circuits for six inverters. Do you see any problems with that app. I have to uncombine them after the switch. I guess as long as the resistance at the other end remains constant it would work. Is it legal?
Not sure if it's legal but don't see why you would need to.
I see no way you could parallel them.
I do, but again, why bother?
We have 6 inverters each needing a positive and a negative. Thats the kicker.
Are ANY of the positives or negatives tied together? If not, then opening one leg for each array will safely disconnect the arrays.
The inspector wants the DC side of the system to be on 1 disconnect for the purpose of giving the fire dept. the luxury of shutting the system down with one handle. This seems impossible! Normally we would have 1 big inverter but not in this case. Any suggestions.
Not impossible, use a pair of 3-pole switches with a mechanical linkage and you've got all six arrays with one handle pull.
But even with only two switches to be pulled it would still meet NEC disconnect requirements as it is far less that the six throws of the hand rule.
And as eprice pointed out, can the inspector produce a written reference for his requirement? If not, tell him politely where to stuff it. No inspector is allowed to make things up just because that's what he personally wants. If that was the case I would ban MWBC's. :grin: