Fionna the thread has, like many, gotten away from the original post. Original post started about RGB LED lighting. I myself took it way in one part about why we size wires different sometimes for dc work, and how when doing dc work we go up in size quicker for voltage drop than many electricians are used to, because of how 12v dc and 24 v dc react to voltage drop.
Very sorry for confusing you.
In the normal consumer world, it is perhaps easiest to simply throw a bunch of inverters into the building, running off a big bank of batteries, and just run everything using 120VAC rules as per NEC, or 240 VAC rules as per UK or EU country rules... depending upon where the building will be, and what you are allowed to do.
However, there is a lot of waste in doing that and this means you must over size your battery systems, and your solar or wind or water generation systems, to account for the waste in the inverters. Some of that waste is able to be in part forgotten about by not using inverters for what you do not need to invert, because enough replacement items are available. One area is lighting.
Case in point... You install lighting in bathrooms and ceilings and kitchens using low voltage lighting that requires transformers to go from local AC to 12 volts. You are using solar on the building and have a 12 volt battery bank powering a 120 volt inverter. So, knowing there is loss in the transformer from 120 volt AC to 12 volt DC in the wiring, and also knowing there is loss in obtaining the 120 volt AC from the battery bank via the inverter, do you then wire 12 volts directly from the battery bank to the lighting, thus reducing loss? Or do you just accept the losses?
Currently the answer is Accept the losses, not just because it is easiest but because of two additional factors... Cost of wiring for the 12 volt voltage drop, and the fact it is very hard to find switches rated for the constant use in 12 volt dc systems that look nice for residential and even commercial use. You say then just use nice looking AC switches but they will not hold up due to ARCing... I am not an expert but am simply learning this vast thing called Electrical work, but, from my own forays into off grid living, I can tell yyou that arcing is a problem when using AC switches on DC circuits.
However, some people wire like I do, as far as trying to get around such things, and do use 12 and 24 volt circuits where lighting does not need turned on and off all the time, or where there are other control methods. Methods such as relays.
Sorry again for taking this circuit off what it was asking.