Hi,
I'm on a dilemma. I want to have the DC ground electrode system to have an alternative in case the inverter is removed (690.49). As summary of the design, this is a flat rooftop system I have DC disconnects on every CB and they land on a pull box before they are routed from the roof to underground and to the inverter. For the GE system I have a ground plate that connects the inverter, main disconnect, existing building ground (is accessible) and a new ground rod.
So my suggestions are:
1. have a busbar on the pull box (NEMA 4) and bong the EGC from the CBs and have that busbar bonded to a GEC (#6 AWG Cu) and route it to the ground bar at ground level.
2. have a GEC going directly from the CBs (#6 AWG Cu) to the ground bar at ground level
My question is if I can actually place a busbar on a pull box and land my ECG there. I don't mind to continue the ground to the inverter and have it just irreversibly spliced and bonded to the pull box busbar instead of terminated there.
Thank you,
I'm on a dilemma. I want to have the DC ground electrode system to have an alternative in case the inverter is removed (690.49). As summary of the design, this is a flat rooftop system I have DC disconnects on every CB and they land on a pull box before they are routed from the roof to underground and to the inverter. For the GE system I have a ground plate that connects the inverter, main disconnect, existing building ground (is accessible) and a new ground rod.
So my suggestions are:
1. have a busbar on the pull box (NEMA 4) and bong the EGC from the CBs and have that busbar bonded to a GEC (#6 AWG Cu) and route it to the ground bar at ground level.
2. have a GEC going directly from the CBs (#6 AWG Cu) to the ground bar at ground level
My question is if I can actually place a busbar on a pull box and land my ECG there. I don't mind to continue the ground to the inverter and have it just irreversibly spliced and bonded to the pull box busbar instead of terminated there.
Thank you,